Fault device likely culprit in Plumpang depot explosion
The Jakarta Post, Jakarta | Tue, 01/20/2009

Preliminary results from the investigation into Sunday's Pertamina fuel depot blaze showed the fire was caused by a faulty tank safety valve, a National Police spokesperson said Tuesday.

"Fire was caused by pressure build-up inside the tank that could not be alleviated by the tank's safety valve," Insp. Gen. Abubakar Nataprawira said, as reported by tempointeraktif.com.
He confirmed there was no indication of foul play or terrorism.

"This is confirmed because no evidence of explosives have been found in tank 24 nor in the area surrounding the tank," Nataprawira said.

The investigation was conducted by a multi-agency team consisting of the National Police forensic lab, Pertamina, and the Downstream Oil and Gas Regulatory Body (BPH-Migas).

Previously, Pertamina corporate secretary Toharso had explained each tank had three safety mechanisms: a sprinkler, an external liquid fire extinguisher and a chemical fire extinguisher.

"There is also a release valve on top of the tank which functions as a decompressor to reduce pressure within the tank whenever fuel is entering or leaving," he said.

Nataprawira added, however, the discovery of a body -- first reported to likely be a security guard -- near the tank could well change preliminary conclusions of the investigation, especially since a mobile phone unit was also discovered nearby.

"That evidence could well be cause for further investigation," he said.(amr)