Incident Report
Subject: Tesoro Anacortes Incident Citations
Date
of Email report: Tue 02/11/2010
Report Detail:
The final two findings in the citations will be of particular note to JOIFF members. Ask yourself the question - are your fire-fighters participating in certified hot fire training and regular gun drills on site? Is the training competence certified or simply attendance based?
Overview
- 2 parallel banks of 3 feed / effluent exchangers;
- SS lining in top shells and first 4’ of 2nd shells (spec break);
- 2nd shell on one bank (Unit E) failed in the carbon steel portion;
- the failure mechanism was high temperature hydrogen attack (HTHA)
Other Facts Inferred
- Inspections of shells was deferred beyond 10 years which did not meet internal procedures or code;
- there was history of S/U leaks on the flanges between hot shells – clamps installed;
- there were changes to the warm up piping used on start up (not clear what);
- it is not clear how warm up piping or start up procedures impacted the failure
Citation Overview
- $2.4 MM Penalty
- 44 Citations – 39 Willful, 5 Serious
- Willful Citations Avg Penalty is $60K - 97% of Penalty
- Tesoro plans to contest the citations
Willful Citations Summary
- Mechanical Integrity (15 citations)
- Inspection procedures did not follow RAGAGEP – 4 xers
- Failure to follow inspection procedures (2 procedures – 2 xers)
- Inadequate wet-mag inspection frequency – 4 xers
- Failures to correct MI deficiencies – warm up line, A/B & D/E xer companion flanges and temp clamps
- Operating Procedures/Operator Training (8 citations)
- Employees inadequately trained in op procedures
- Did not develop & implement written start up procedure
- MOC (7 citations)
- Op procedures changes for warm up line & s/u procedure, min limit on H2/oil change, mechanical clamps, corrosion awareness program changes
- PHA revalidation process excluded corrosion/MI review,
- inspection procedure not followed
- PHA (1 citations)
- PHA reval process not followed,
- Other (9 citations)
- Inadequate PPE – each of 7 persons killed
- Failure to update PSI,
- Failure to investigate incidents (related to leaks
Serious Citations Summary
- Did not ensure warm up lines were installed properly
- Did not ensure the E-6600 bellows assemblies were adequate for the service
- Did not ensure operators understood training on the E-6600 start up procedure
- Emergency responders did not coordinate all communications through the IC
- Fire Brigade member did not have live fire training or participate in drills
|