Report Detail: |
The National Transportation Safety Board has issued its
report on the cause, consequences, and recommendations related to the
tank fire on April 7, 2003 at ConocoPhillips' Glenpool South tank farm
in Glenpool, Oklahoma. The tank was being filled with diesel after having
been drained of gasoline.
The report's key findings leading to the explosion are as follows (summarized
from page 39 of the attached report):
- The tank was switch loaded at flow velocities significantly higher than
those in the company procedures and industry-recommended practices.
The high velocity of the diesel in the tank fill piping and turbulence
created in the sump area resulted in the generation of increased static
charge.
- Operations from April 4 to 7, which included a partial draining that
landed the floating roof and partial fillings before draining dry, allowed
a large amount of gasoline vapor to be generated and distributed within
the tank to create a flammable fuel-air mixture both above and below the
floating roof.
- The NTSB also found that the situation was worsened due to the American
Electric Power responder not coordinating his actions with the incident
command staff, and not shutting down power to their lines. The lines eventually
fell into the pooled diesel and a new fire resulted.
The NTSB recommends that RSPA (as they were known at the time):
- Revise the emergency response planning requirements in the pipeline safety
regulations to include coordination with electric and other utilities
that may need to respond to a pipeline emergency.
- Issue an advisory bulletin to liquid pipeline operators to validate the
accuracy of their tank strapping tables.
The NTSB recommends that ConocoPhillips:
- Revise their storage tank operating procedures to include instructions
for minimizing the possibility of creating a flammable atmosphere and
the occurrence of a static discharge inside a tank after a floating roof
has been either intentionally or unintentionally landed, especially for
tanks where switch loading is likely to occur.
- Evaluate their storage tank operating procedures and make the revisions
necessary to ensure that product flow rates in both the tank fill line
and the discharge nozzles are restricted to provide a level of protection
against excess static electricity that is at least commensurate with industry
standards.
- Revise their emergency response plan to include preplanning with nearby
electric facilities, where applicable.
View / download full report on: NTSB Glenpool Tank Farm Incident (PDF doc) |